eratic temperature reading on EMON 2H1A moniter

PostPosted: Fri Jun 14, 2013 1:15 pm
by schorn
Without any changes made to battery system the temperature on the monitor fluctuated between 15 degrees F to 80 Degrees F. I replaced the 2018 probe going to the battery and checked the voltage on TB1 #6 & #9 and it read 3.02 volts, which is in spec. (temperature was about 82 degrees F).
What else could be causing the fluctuation?

Re: eratic temperature reading on EMON 2H1A moniter

PostPosted: Fri Jun 14, 2013 2:52 pm
by Coulomb
Disconnect power from the unit for a few seconds and see if that cures the problem.