17 volts at a 12 volt battery bank???

This forum is for general electrical issues. See other forums for product specific issues

17 volts at a 12 volt battery bank???

Postby johnrosendale on Wed Mar 10, 2010 10:34 am

I have two battery banks on my boat. With the AmplePower alternator running, and an amplepower 3-step regulator, I get 14.6 volts on one bank and 17 volts on the other. I get 13 volts without the alternator running on each bank. Any idea why I would be getting 17 volts? Could this be a problem with a bad battery bank?
johnrosendale
 
Posts: 13
Joined: Tue Feb 16, 2010 1:43 pm

Re: 17 volts at a 12 volt battery bank???

Postby Coulomb on Wed Mar 10, 2010 3:34 pm

It sounds like you're charging through a battery selector switch. The regulator is sensing battery voltage on one bank, and not the other.
Try charging in both.

What model is the regulator.
Coulomb
Site Admin
 
Posts: 1174
Joined: Sat Jun 06, 2009 5:11 pm

Re: 17 volts at a 12 volt battery bank???

Postby johnrosendale on Thu Mar 11, 2010 9:26 am

It's a Model #1021-A Deep Cycle Regulator. I've noticed the voltage/temperature sensors are only attached to the bank of batteries that charges at 14.6 volts. Could this be why the other battery bank is charging through the switch at 17 volts? because the regulator doesn't recognize the increase in voltage from the alternator at that bank of batteries? Or could it be a bad cell in the battery bank?
I'm wondering... maybe I should tie the voltage/temperature sensor into both banks. Your thoughts?
johnrosendale
 
Posts: 13
Joined: Tue Feb 16, 2010 1:43 pm

Re: 17 volts at a 12 volt battery bank???

Postby Coulomb on Thu Mar 11, 2010 11:49 am

The #1021 regulator was made in the 1980s, but there are lots of them still doing a great job charging batteries.

It requires a #1018 voltage/temperature sensor on each battery bank to be charged independently.

You can contact Ruth to order a replacement sensor.
Coulomb
Site Admin
 
Posts: 1174
Joined: Sat Jun 06, 2009 5:11 pm

Re: 17 volts at a 12 volt battery bank???

Postby johnrosendale on Thu Mar 11, 2010 1:10 pm

So is this 1018 more than a simple 18 guage insulated wire? The one that I currently have running to one battery bank appears to be a simple wire without a "sensor".

Also, on the back of the Amplepower alternator there is a wire running from the positive output lug to ground on the alternator. It appears that somekind of a device is on circuit. What is this for?

You've been very helpful. Thank you!!
johnrosendale
 
Posts: 13
Joined: Tue Feb 16, 2010 1:43 pm

Re: 17 volts at a 12 volt battery bank???

Postby johnrosendale on Thu Mar 11, 2010 1:10 pm

So is this 1018 more than a simple 18 guage insulated wire? The one that I currently have running to one battery bank appears to be a simple wire without a "sensor".

Also, on the back of the Amplepower alternator there is a wire running from the positive output lug to ground on the alternator. It appears that somekind of a device is on circuit. What is this for?

You've been very helpful. Thank you!!
johnrosendale
 
Posts: 13
Joined: Tue Feb 16, 2010 1:43 pm

Re: 17 volts at a 12 volt battery bank???

Postby Coulomb on Thu Mar 11, 2010 4:25 pm

There's a sensor potted in the battery lug.

The itme on the back of the alternator is a transient absorber, called a snubber.
Coulomb
Site Admin
 
Posts: 1174
Joined: Sat Jun 06, 2009 5:11 pm

Re: 17 volts at a 12 volt battery bank???

Postby johnrosendale on Wed Mar 17, 2010 11:13 am

What is the "snubber" used for?
johnrosendale
 
Posts: 13
Joined: Tue Feb 16, 2010 1:43 pm

Re: 17 volts at a 12 volt battery bank???

Postby Coulomb on Thu Mar 18, 2010 10:38 am

It may protect the alternator from failure when the 1-2-both switch opens either manually or from overheating. See this URL: http://www.amplepower.com/apps/burnt_sw/index.html
Coulomb
Site Admin
 
Posts: 1174
Joined: Sat Jun 06, 2009 5:11 pm


Return to General Electrical