Multiple Shunt Installation

PostPosted: Wed Jan 19, 2011 3:49 pm
by Gary
I currently have a shunt on the negative line close to the negative distribution post for an Emon and V2 regulator. I’ve just installed an inverter/charger that wants a battery monitoring kit installed for better battery management. The kit requires a shunt to be installed in the same vicinity as the existing shunt. If I install a second shunt within close proximity to the existing Ample Power system shunt will this yield a problem?

Thx, Gary

Re: Multiple Shunt Installation

PostPosted: Wed Jan 19, 2011 4:31 pm
by Coulomb
If they use the same shunt, 50 mV at 400 Amps, you can use one shunt. Otherwise, connect them in series.

Re: Multiple Shunt Installation

PostPosted: Wed Jan 19, 2011 10:18 pm
by Gary
Thanks for the response. Their shunt is a 50mV at "500amps" and I have emailed them for compatibility with the established Ample Power 400amp unit. Regards, Gary

Re: Multiple Shunt Installation

PostPosted: Thu Jan 20, 2011 1:34 am
by Coulomb
You'll have to wire the shunts in series.