I have two SAR v3's on my boat, one is running from the main engine that has two alternators, this one seems to be working fine. The other is on a Genie type 12 generator that has a 130 amp alternator. This one is not so fine. My battery bank consists of three 8d gel ample power batteries giving a total ah of about 675 ah. I discharged the bank to 50% and attempted to charge using the Genie. This worked until it went into float leaving 135 ah remaining. I never saw the volts on the EM II go above 13.83. After reading the trouble shooting instructions I discounted the battery thermocouple for the Genie's V3. Starting the generator again I saw a rise in volts to 14.01 and a few more ah's. The dip switches are all up.
I might add that the Genie although fitted by the PO some years ago has only 3.5 hours running.
I'm zguessing that the V3 might be faulty. Can you comment?

Re: SAR V3

PostPosted: Tue Jul 02, 2013 11:35 am
by Coulomb
If it's regulating at all, the SARV3 is working. Probably the EMON and the batteries are out of sync.

Re: SAR V3

PostPosted: Tue Jul 02, 2013 6:51 pm
by Bazz
Can you suggest how to them on sync ?

Re: SAR V3

PostPosted: Wed Jul 03, 2013 1:22 am
by Coulomb
There's a section in the Emon manual about accuracy which should explain what to do.

Re: SAR V3

PostPosted: Mon Aug 26, 2013 4:44 pm
by Bazz
I think I have discovered the cause of my problem. The alternator is producing the correct voltages, but due to the length of the battery cables, I am getting ..6 volt drop between the alternator and the battery bank. The sense wire is close to the alternator on a distribution post. Do you suggest moving the sense directly to the battery positive?

Re: SAR V3

PostPosted: Tue Aug 27, 2013 7:50 pm
by Coulomb
Yes.

Re: SAR V3

PostPosted: Sun Sep 01, 2013 3:01 am
by Bazz
Can the sav 3 ground wire also go direct to the battery negative post? I am also getting a voltage difference between the negative distribution post and the battery negative.

Re: SAR V3

PostPosted: Mon Sep 02, 2013 2:45 pm
by Coulomb
Yes, the voltage that's important is the battery, not what shows up at distribution.