Voltage Runaway

PostPosted: Mon May 28, 2012 8:05 am
by malon
Hello,

I'm getting voltage runaway alarm when running the engine after a solar panel install. The voltage limit on the solar controller is 14.4. Can I use the voltage adjustment on the next step regulator to set the set-point a bit higher than 14.4 so that I will not reach the alarm threshold?

Thanks
Sean

Re: Voltage Runaway

PostPosted: Tue May 29, 2012 3:45 pm
by Coulomb
You can set the voltage higher, but it may destroy your batteries. Disconnect the solar panels when the engine is running.

Re: Voltage Runaway

PostPosted: Thu Jun 07, 2012 1:35 pm
by malon
I see. If I could ask another question please. When measuring absorbtion voltage, the voltmeter negative lead is on GND and the voltmeter negative lead should be on Batt volts on the regulator? May sound like a strange question, I just want to make sure.

Thanks for all the advice.

Sean

Re: Voltage Runaway

PostPosted: Thu Jun 07, 2012 2:37 pm
by Coulomb
If you wired according to the instructions, just read the voltage across the battery and then at the regulator. They should be essentially the same.