Setting Max Amps

Postby dvkall on Mon Jan 24, 2011 4:09 pm

I have a EMON and the SAR V3 regulator with the Dual controler. I would like to set my alternator to max at 150 amps. I can't find the setting in the EMON manual and when I try to adjust it in the regulator I seem to get no response. Everything else being equal, the regulator appears to work fine running through all 3 stages when I run the generator long enough.

Thanks
dvkall
 
Posts: 20
Joined: Wed Aug 19, 2009 6:48 am

Re: Setting Max Amps

Postby Coulomb on Tue Jan 25, 2011 3:19 pm

The Emon does not provide Amps limit with the SAR V3. You need to do that using the limiting feature of the regulator itself.
Coulomb
Site Admin
 
Posts: 1174
Joined: Sat Jun 06, 2009 5:11 pm

Re: Setting Max Amps

Postby dvkall on Wed Jan 26, 2011 12:19 pm

Thanks,
Now I've tried a couple of turns (both ways on the SAR). If I turn the screw clockwise all the way is that limiting the amps? Sorry if I'm confused but when I've tried 2 turns one way and then 4 turns the opposite I don't see any results?

Appreciate your website and this form.

Thanks again.
Dave
dvkall
 
Posts: 20
Joined: Wed Aug 19, 2009 6:48 am

Re: Setting Max Amps

Postby Coulomb on Wed Jan 26, 2011 1:19 pm

You have to put the internal jumper in place to activate current limiting.

The pot is 10 turns. Clockwise increases current. You won't see a difference when the voltage is at the charge set point, because the demand for current is, by definition, less than the limit value.
Coulomb
Site Admin
 
Posts: 1174
Joined: Sat Jun 06, 2009 5:11 pm