I'm working through an issue with an Emon2-h1 and solar relay. The solar relay is installed as per the supplied diagram and tested by asserting EM relay pin 1-1 high to trigger the relay. I confirmed the EM relay switches the load properly.
The problem I'm having is when I connect Em relay 1-1 to the Emon 2-1 slr, I can't get the slr output to switch at all.
I set the volts lo at 13.4 and volts hi at 13.7. I then switched the battery charger on and off several times and watched the voltage rise past the volts hi setpoint then fall below the volts lo setpoint. As I understand it, the relay should switch back and forth as I run the voltage up and down with the charger past the programmed setpoints.
I disconnected the EM relay from the 2-1 slr output and metered pin 2-1on the emon. The voltage reads minus 7.21Vdc referenced to neg distribution. The voltage doesn't toggle at all as I run the system voltage up and down.
Other settings are temp compensation - false, B1 full - false. It should be in solar mode.
Is there anything in the programming I'm missing or does it sound like a problem with the Emon?
Any thoughts on where the problem might be would be appreciated